Regardless of whether the armouring of the cable serves as a protective conductor, or not, it should always be effectively earthed to ensure the requirements of ADS are met. Should the armouring not be effectively earthed and a fault develops due, for example, to mechanical damage of a line conductor incorporated in the cable, the condition may leave the armouring attaining line voltage and pose a danger to persons in the vicinity of the installation or using the installation.
https://www.voltimum.co.uk/articles/guide-installing-steel-wired-armoured
Can anyone post a link to what seems to be an authoritative article saying that it’s not required? There’s plenty of “how to do it” videos on Youtube in which electricians say it’s not required, but I don’t count consider those authoritative.
Btw – domestic – through cavity wall to outside.
Just out of interest, please give more details. Length of run. Height above ground. Is the cable liable to receive knocks or thumps by anything? What does it run to? Why was S.W.A. chosen in the first place for this run? Have you any pictures of the run.
Thanks,
Z.
It’s easy to find guidance telling electricians to earth the armour of SWA cables, such as this: Providing automatic disconnection of supply (ADS)
So as far as I am concerned SWA has single insulated conductors within metal containment and that metal containment needs to be earthed