IEC 60364 Table 48A

Former Community Member
Former Community Member
Does anyone know where I can find table 48A? I am reading of its existence, but don't know where to find it.
Parents
  • Former Community Member
    0 Former Community Member
    mapj1:

    It was called 48A in the older withdrawn versions, then in 2001 it became
    Table 41C (48A) – Maximum disconnecting times in the then new  Electrical installations of buildings Part 4-41:

    in the 2005 version it became Table 41.1 – Maximum disconnection times

    As far as I know the numbers have not changed at all for years, and we are now in the 2017 edition.

    The figures in the UK regs are a direct copy without the bits for 120V land.


    89049e5216f57b156a8e1e2ec5e99247-original-41-1capture.png




    From what I gather, the disconnection times were faster in 48A for certain locations by a factor of half.

    d402d3cb71d69878be4d648eee764545-original-image-20210531094627-1.png


Reply
  • Former Community Member
    0 Former Community Member
    mapj1:

    It was called 48A in the older withdrawn versions, then in 2001 it became
    Table 41C (48A) – Maximum disconnecting times in the then new  Electrical installations of buildings Part 4-41:

    in the 2005 version it became Table 41.1 – Maximum disconnection times

    As far as I know the numbers have not changed at all for years, and we are now in the 2017 edition.

    The figures in the UK regs are a direct copy without the bits for 120V land.


    89049e5216f57b156a8e1e2ec5e99247-original-41-1capture.png




    From what I gather, the disconnection times were faster in 48A for certain locations by a factor of half.

    d402d3cb71d69878be4d648eee764545-original-image-20210531094627-1.png