IEC 60364 Table 48A

Former Community Member
Former Community Member
Does anyone know where I can find table 48A? I am reading of its existence, but don't know where to find it.
Parents
  • Former Community Member
    0 Former Community Member
    gkenyon:
    mapj1:

    It was called 48A in the older withdrawn versions of 60364-4-41 , then in 2001 it became
    Table 41C (48A) – Maximum disconnecting times in the then new  Electrical installations of buildings Part 4-41:

    in the 2005 version it became Table 41.1 – Maximum disconnection times

    As far as I know the numbers have not changed at all for years, and we are now in the 2017 edition.

    The figures in the UK regs are a direct copy without the bits for 120V land.


    89049e5216f57b156a8e1e2ec5e99247-original-41-1capture.png


    Hang on ... in 2001 edition, Table 41C (48A) is NOT an equivalent of what we have now in Table 41.1. It only applied in cases where the relevant part 7 (IEC 60364-7-7xx) reduced the maximum permissible touch voltage via equipotential bonding to 25 V AC or 60 V DC. See C|Lauses in 413.2 of the 2001 version.


    For TN systems under usual conditions, see Table 41A and 41B of that standard ... which became what we now have as Table 41.1.







    Do you have a copy of the table?


    My understanding is that there is a 50 volt and a 25 volt touch limit based on the environment.


Reply
  • Former Community Member
    0 Former Community Member
    gkenyon:
    mapj1:

    It was called 48A in the older withdrawn versions of 60364-4-41 , then in 2001 it became
    Table 41C (48A) – Maximum disconnecting times in the then new  Electrical installations of buildings Part 4-41:

    in the 2005 version it became Table 41.1 – Maximum disconnection times

    As far as I know the numbers have not changed at all for years, and we are now in the 2017 edition.

    The figures in the UK regs are a direct copy without the bits for 120V land.


    89049e5216f57b156a8e1e2ec5e99247-original-41-1capture.png


    Hang on ... in 2001 edition, Table 41C (48A) is NOT an equivalent of what we have now in Table 41.1. It only applied in cases where the relevant part 7 (IEC 60364-7-7xx) reduced the maximum permissible touch voltage via equipotential bonding to 25 V AC or 60 V DC. See C|Lauses in 413.2 of the 2001 version.


    For TN systems under usual conditions, see Table 41A and 41B of that standard ... which became what we now have as Table 41.1.







    Do you have a copy of the table?


    My understanding is that there is a 50 volt and a 25 volt touch limit based on the environment.