IEC 60364 Table 48A

Former Community Member
Former Community Member
Does anyone know where I can find table 48A? I am reading of its existence, but don't know where to find it.
Parents
  • ProMbrooke:
    af0b2ad8bb5ed502836b80c425799d16-original-image-20210531124229-2.png

    b1b457822aa81b1d8d92556ddb074efc-original-image-20210531124108-1.png


    Yes ... these ignore the supplementary protective measures in Sections in Part 7. As per previous post.


    So Section 701, before 2008, limit of touch voltage = 50 V, so disconnection time = 5 s as per your table for humid condition above.  After 2008, either limit of touch voltage = 50 V, or RCD protection = better disconnection time. Mains not permitted in bathtub (zone 0) itself.


Reply
  • ProMbrooke:
    af0b2ad8bb5ed502836b80c425799d16-original-image-20210531124229-2.png

    b1b457822aa81b1d8d92556ddb074efc-original-image-20210531124108-1.png


    Yes ... these ignore the supplementary protective measures in Sections in Part 7. As per previous post.


    So Section 701, before 2008, limit of touch voltage = 50 V, so disconnection time = 5 s as per your table for humid condition above.  After 2008, either limit of touch voltage = 50 V, or RCD protection = better disconnection time. Mains not permitted in bathtub (zone 0) itself.