IEC 60364 Table 48A

Former Community Member
Former Community Member
Does anyone know where I can find table 48A? I am reading of its existence, but don't know where to find it.
Parents
  • Thus, I am advocating for a touch voltage limit of 25 volts be established for wet locations with a disconnection time of at most 0.2 seconds for 230 volt supplies.

    Curiously, we seemed to have exactly that for some special locastions back in the 16th Ed (1991) - specificslly construction sites (section 604) and Agricultural and Horticultural Premises (section 605) - so somewhere along the line it seems that someone decided that 0.4s plus additional protection (e.g. 30mA RCDs) was an improvement.


    Perhaps oddly the same requirements didn't appear for bathrooms or pools at the time, even though there was no requirement for RCDs (although 230V was banned from the wettest part of those locations and supplementary bonding was required).


    It's perhaps a mute point anyway, since most final circuits are protected by B-type or C-type MCBs (or similar in RCBOs) - so disconnection will be within 0.1s anyway (and 0.04 if a 30mA RCD is functioning) - so a change to 0.,2s in the regulations perhaps wouldn't result in any significant safety improvement in practice.


       - Andy.
Reply
  • Thus, I am advocating for a touch voltage limit of 25 volts be established for wet locations with a disconnection time of at most 0.2 seconds for 230 volt supplies.

    Curiously, we seemed to have exactly that for some special locastions back in the 16th Ed (1991) - specificslly construction sites (section 604) and Agricultural and Horticultural Premises (section 605) - so somewhere along the line it seems that someone decided that 0.4s plus additional protection (e.g. 30mA RCDs) was an improvement.


    Perhaps oddly the same requirements didn't appear for bathrooms or pools at the time, even though there was no requirement for RCDs (although 230V was banned from the wettest part of those locations and supplementary bonding was required).


    It's perhaps a mute point anyway, since most final circuits are protected by B-type or C-type MCBs (or similar in RCBOs) - so disconnection will be within 0.1s anyway (and 0.04 if a 30mA RCD is functioning) - so a change to 0.,2s in the regulations perhaps wouldn't result in any significant safety improvement in practice.


       - Andy.