Does anyone know where I can find table 48A? I am reading of its existence, but don't know where to find it.
  • Former Community Member
    0 Former Community Member
    Zoomup:
    ProMbrooke:
    Zoomup:
     




    I've long proposed discarding the emphasis/focal point of earthing and bonding and rather creating a new, third central pillar of source loop conduction theory, which rooted in admittance on the basis of protecting life and property rather than having earth electrodes and connecting metal things to one another.





    What is "source loop conduction?". How does it work? Or is it just something that The Dr. and Rose Tyler would come across?


    B.S. 7671 already covers safety of installations.


    Reg. 131.1 "...intended to provide for the safety of persons, livestock and property against dangers and damage which may arise in the  reasonable use of electrical equipment."


    Z.


     




    Source loop conduction is the idea that high admittance between the line and CPC/metal work at any point that a fault  is capable of occuring can trigger disconnection of the over current device rapidly enough to prevent physiological harm and fire to the property.


    Basically a more evolved theory of ADS.


    I know BS7671 covers protection of life and property.




    I'll stick with the approved, tried and tested systems in place at present thanks, not some unproven, unconvincing and unworkable "theory".


    Z.







    Then we can be friends :)


  • Former Community Member
    0 Former Community Member
    Zoomup:
    ProMbrooke:

    Also this video. Most importantly around 25 minutes in, the author shows a breaker tripping magnetically vs thermally:



    https://www.youtube.com/watch?v=emxfsOUTkUg


    Yeh, but the fire was started by a propane torch not an electrical arc. Why worry about electrical arcs when the fire has already been started by another cause? Illogical.


    Edit, add.


    In the U.K. we have the wonderful 13 Amp. plug made to B.S. 1363. Have you ever heard of it? It contains a fuse. The fuse rating can popularly be either 3 Amp or 13 Amp, but other sizes are available like 5 Amp or 10 Amp. Flexes are protected by these fuses which are less in value than the 20 Amp circuit breakers referred to in the dated video.


    Z.







    Illogical indeed, but sadly this was enough to get AFCIs taken seriously.


    Of course I've heard of BS 1363 plugs. AFCIs were supposed to to mimic their their ability of clearing flex faults rather quickly.


  • Former Community Member
    0 Former Community Member
    AJJewsbury:
    Source loop conduction is the idea that high admittance between the line and CPC/metal work at any point that a fault is capable of occuring can trigger disconnection of the over current device rapidly enough to prevent physiological harm and fire to the property. Basically a more evolved theory of ADS.

    It sounds like the ADS part of the old EEBADS approach - or is there more to it than that?


    (I've got in the back of my mind that Earthing is more than just about triggering ADS - it also keeps the entire LV system at a known voltage w.r.t. the general mass of the earth, and prevents it being dragged to other voltages by other systems - e.g. by capacitive coupling to HV circuits via the supply transformer, or other near-by systems -  protecting not just people from shock by the insulation of the conductors too.)


      - Andy.





    Can you go into more detail on the EEBADS approach?


  • Former Community Member
    0 Former Community Member
    mapj1:

    The thing about the Pace consulting notes and the you tube videos is that they relate to 110V land, where installation practices are very different. 

    I do not think you could set fire to a UK extension lead in a cardboard sandwich  and expect it to remain live and sizzling for very long at all, certainly only a few seconds, not minutes.

    230V land regulations actually require us to verify Zs, and the L-N equivalent when we test PSSC, and that coupled with the maximum voltage drop specification, pretty much assures that any LN or LE  short circuit or fault of fractional ohms will trip the breakers quite promptly. The higher voltage lower current also helps with that.

    Now of course there are always corner cases that will struggle, one might be a 50m extension lead snaking down the garden in skinny 1.5mm2 cable - being near that 16 AWG example,  perhaps plugged into a socket already marginal on voltage drop at full load. (so about an ohm there and back in the cable), and if the VD to the socket is the max of 5% (12V) at 13A (then a further ohm or so for that)  Here the PSSC at the end of the extension lead may be as low as 100A.

    However while the 32A C type will be well on the thermal curve and may not fire until about 10 seconds, it is more likely to be a B type, and that will prompt -trip in many cases, and even if it does not, then the  13A fuse in the plug will get you within 3 seconds at 100A.


    The US centric sizzling faults are not the kind seen here - the cables that stay live tend to blow to clear.

    Mike





    Alright, it seems we're all on the same page. And I'll add that not only is EFLI  is none existent in NFPA-70, but the CPCs are also grossly under sized. Just don't say that on a US forum.


    So my question is: why are AFDDs being mandated through out the IEC market place?


  • Can you go into more detail on the EEBADS approach?

    You're making me feel old now!


    EEBADS = Earthed Equipotential Bonding and Automatic Disconnection of Supply - what ADS was referred to in years gone by (but long after the period where regs required some earthing, and perhaps a limit on the resistance between parts within an installation, but without any particular requirement for disconnection). The EEB bit got dropped from the name - possibly due to the fact that bonding doesn't really create a true equipotential zone (at least not where large fault currents are involved - Ohm's Law gets in the way), plus of course we sometimes don't even attempt to create an equipotential zone (outdoors for instance), but still have ADS.


       - Andy.
  • Former Community Member
    0 Former Community Member
    AJJewsbury:
    Can you go into more detail on the EEBADS approach?

    You're making me feel old now!


    EEBADS = Earthed Equipotential Bonding and Automatic Disconnection of Supply - what ADS was referred to in years gone by (but long after the period where regs required some earthing, and perhaps a limit on the resistance between parts within an installation, but without any particular requirement for disconnection). The EEB bit got dropped from the name - possibly due to the fact that bonding doesn't really create a true equipotential zone (at least not where large fault currents are involved - Ohm's Law gets in the way), plus of course we sometimes don't even attempt to create an equipotential zone (outdoors for instance), but still have ADS.


       - Andy.




    Thanks :)


    And I agree much that same with all your points.


  • Before the RCD was as reliable as it is today,  the EEB part was taken more rigorously.

    From

    15th Edition Regulations (1981) 

    Regulation 413.7 required metal parts within the equipotential zone to be supplementary bonded to maintain the equipotential zone, where those parts:



    1. Are extraneous-conductive-parts, and

    • Are simultaneously accessible with exposed-conductive-parts or other extraneous-conductive-parts, and

    • Are not electrically connected to the main equipotential bonding by permanent and reliable metal-to-metal joints of negligible impedance.


    Now the keen can read that so you need to bond the door handle to the toothbrush holder in the bathroom  if less than say 6 ft apart, and some folk did rather run away with that sort of thing, and a lot a green and yellow wire was sold and installed in places that confuse the younger electricians, bonding taps to metal window frames and so on.

    This pic is copied from (another post) and shows the "best practice" of the time.

    Being the UK that means almost no-one did it completely correctly.

    Had it been Germany it would have been like this in every house, had it been somewhere sunnier  no-one would have bothered at all. What you find in reality is sort of in between those extremes.


    Note all those dotted lines are supposed to be equipotential bonds.  (Oddly except the pull cord light switch - perhaps they assumed that the string had broken and been replaced by an offcut of earth wire... quite possible in the 1970s I suppose.)

    Note this a bit of an artists impression, and not all older houses had massive kitchens and bathrooms and no electricity in sleeping accommodation or living rooms, and although not shown, most post war buildings had toilets inside, & in others  the outside one would have been upgraded to electricity for lighting at least ... ?


    Mike.


    EEBADS at peak enthusiasm..




  • Former Community Member
    0 Former Community Member
    Thank you for this! Enthusiasm peaked :) ?



    Kind of reminds me of US practices where a ground riser is run through none steal frames buildings so all separately derived sources can be connected to a common electrode.


    The thing is, looking at your graphic, I wonder if any copper is really saved. All the copper that goes into bonding everything together locally could go into a larger CPC whereby touch voltage is reduced in addition to disconnection times via fuses. It would also make compliance much easier in that I can not see any of that being done to the letter or remaining that way as plumbers/builders change things.


    Extremes are the worst IMO, in that you energize more metal parts relative to those which are not bonded.





  • I wonder if any copper is really saved. All the copper that goes into bonding everything together locally could go into a larger CPC whereby touch voltage is reduced in addition to disconnection times via fuses


    Oh no saving at all really. The big problem with your idea is that is that the CPC to the light above the sink does not  go to the taps at all, unless you bond it, and the 'equipotential'  idea here was that during fault it all flashed live together, and the hapless user feels no shock because he and everything he can possibly touch is at the same voltage, so you can afford an upper limit of 5 seconds for the fuse to blow. Bit like the bird on the LV cable. Some single phase O/H TT for you here.

    Note that this pole could not be made PME without some changes to the cable arrangement.






    Note I say 5 seconds, not 0.4 - that faster limit applied to the ccts in the bathroom, but not to everything sharing the same CPC and plumbing, so a fault in the bedroom, left  of picture, ( note the bond to the metal bits of the fire place - did anyone ever do that, really ?) could perhaps take anything up to 5 seconds to clear with extension leads and a defective heater or something,  - and the whole bathroom may go up with it as well, as the radiator pipes are shared. Pity about the poor old window cleaner touching the same live for 5 seconds window frames from outside of course....


    And the fact is that a new installation probably met all the resistance test limits for all of about a week until someone changed the taps, or the radiator or something  led to the whole concept falling to one side a bit.

    And it is no damn good having live taps and all that jazz if you are standing on a modern concrete floor either. The traditional floor boards  with a 2 foot airgap work really well but solid floors downstairs are a bit more variable.

    So now we drop the EEB, fit an RCD to get the breaking time down for all circuits, not just bathrooms, and it is just called ADS.

    Mike.
  • Former Community Member
    0 Former Community Member
    Right, there will be huge difference in potential. Thats where 0.25 seconds come in, in that harm can not take place with 125 volts between the hands or hands and feet persisting for only a fraction of a second. 


    IF the fault is through a heating element, the resistive divider math still applies. A 20 amp type B  MCB has an EFLI of 1.84 ohms. Assuming an R1+R2 of 1.49, we have an R2 of 0.745.  4000/230=17 amps or a 13 ohm resistance. Assuming the fault is at midway through the element, 6.5 ohms plus 0.745 ohms = 7.245 ohms. Using a resistive divider, we get 21.4 volts to remote earth.


    Assuming that the fault takes 5 seconds to trip the MCB, 4 x 20= 80 amps or a 2.875 ohm fault.


    0.745ohms + 2.875 ohms = 3.62 ohms. Going by a resistive divider we get 39 volts to remote earth. Below 50 volts, but higher than 25 volts. RCD would help in this case, but so does the full size CPC.



       

    Typically a dead fault would trip an MCB instantly, so the RCD is supplemental protection as it should be. However if fuses are fitted 0.4 seconds would end up being a real thing.