Zs readings over limits

Former Community Member
Former Community Member
Doing an EICR in a block of flats and quite a few of the lighting circuits have excessive Zs readings. All the circuits are on 60898 C10's without RCD protection with readings in the late 2 early 3 ohm range (max permitted 2.19). I know test result fails are generally a code 2 but these are LED panel downlighters with mostly class 2 drivers connected via choc boxes above the suspended ceiling so nothing really accessible. They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR
Parents
  • Former Community Member
    0 Former Community Member
    Alan, of course you are right, under fault conditions ADS has to work to prevent anyone getting an electric shock but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from, the Zs test was made on the unterminated cpc of the T&E cable at the end of the circuit. Suppose the issue would be someone cutting or damaging the cable.
Reply
  • Former Community Member
    0 Former Community Member
    Alan, of course you are right, under fault conditions ADS has to work to prevent anyone getting an electric shock but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from, the Zs test was made on the unterminated cpc of the T&E cable at the end of the circuit. Suppose the issue would be someone cutting or damaging the cable.