Zs readings over limits

Former Community Member
Former Community Member
Doing an EICR in a block of flats and quite a few of the lighting circuits have excessive Zs readings. All the circuits are on 60898 C10's without RCD protection with readings in the late 2 early 3 ohm range (max permitted 2.19). I know test result fails are generally a code 2 but these are LED panel downlighters with mostly class 2 drivers connected via choc boxes above the suspended ceiling so nothing really accessible. They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR
Parents
  • Geez:

    They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR


    I agree with the others - excessive Zs = C2.


    Now all you have to do is decide whether to recommend replacement with C6 or B10.


Reply
  • Geez:

    They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR


    I agree with the others - excessive Zs = C2.


    Now all you have to do is decide whether to recommend replacement with C6 or B10.