Geez:
prob a c6 would be better than a b10 considering surge current nuisance tripping (60A vs 50A)
But MCBs are liable to instantaneously trip anywhere within their multiplier range - 3-5x for a B type or 5-10x for a C-type - thus you need to stay below the lower multiplier when you want an MCB not to trip - hence 30A for a B10 (10x3) or 30A for a C6 (6x5).
- Andy.
Geez:
prob a c6 would be better than a b10 considering surge current nuisance tripping (60A vs 50A)
But MCBs are liable to instantaneously trip anywhere within their multiplier range - 3-5x for a B type or 5-10x for a C-type - thus you need to stay below the lower multiplier when you want an MCB not to trip - hence 30A for a B10 (10x3) or 30A for a C6 (6x5).
- Andy.