Zs readings over limits

Former Community Member
Former Community Member
Doing an EICR in a block of flats and quite a few of the lighting circuits have excessive Zs readings. All the circuits are on 60898 C10's without RCD protection with readings in the late 2 early 3 ohm range (max permitted 2.19). I know test result fails are generally a code 2 but these are LED panel downlighters with mostly class 2 drivers connected via choc boxes above the suspended ceiling so nothing really accessible. They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR
Parents
  • Chris Pearson:
    Geez:

    They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR


    Now all you have to do is decide whether to recommend replacement with C6 or B10.




    Shirley, that is outwith the remit of a report on the condition. ?


    Jaymack


Reply
  • Chris Pearson:
    Geez:

    They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR


    Now all you have to do is decide whether to recommend replacement with C6 or B10.




    Shirley, that is outwith the remit of a report on the condition. ?


    Jaymack