Zs readings over limits

Former Community Member
Former Community Member
Doing an EICR in a block of flats and quite a few of the lighting circuits have excessive Zs readings. All the circuits are on 60898 C10's without RCD protection with readings in the late 2 early 3 ohm range (max permitted 2.19). I know test result fails are generally a code 2 but these are LED panel downlighters with mostly class 2 drivers connected via choc boxes above the suspended ceiling so nothing really accessible. They would all comply with a C6 btw. Just wondered if you'd C2 this resulting in an unsatisfactory EICR
Parents
  • under fault conditions ADS has to work to prevent anyone getting an electric shock but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from, the Zs test was made on the unterminated cpc of the T&E cable at the end of the circuit.

    I can see the point that it could (in theory) be declared a double/reinforced insulation circuit - and the c.p.c. omitted altogether and Zs would be irrelevant (as it's in a common area, rather than domestic, the bit about ensuring adequate supervision could perhaps be complied with).


    With a c.p.c. present however there would seem to be a risk of a L-c.p.c. fault (especially with T&E where the c.p.c. isn't insulated as if it were a live part), which although wouldn't make any exposed-conductive-parts on that circuit live (as there aren't any) - it would make the c.p.c. itself hazardous live - and so too anything connected to it - e.g. exposed-conductive-parts of other circuits connected to the same DB for instance. Granted the touch voltage on remote parts would likely be much lower than at the fault - but if the disconnection time is really extended that still might not be sufficient to ensure safety.


      - Andy.


Reply
  • under fault conditions ADS has to work to prevent anyone getting an electric shock but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from, the Zs test was made on the unterminated cpc of the T&E cable at the end of the circuit.

    I can see the point that it could (in theory) be declared a double/reinforced insulation circuit - and the c.p.c. omitted altogether and Zs would be irrelevant (as it's in a common area, rather than domestic, the bit about ensuring adequate supervision could perhaps be complied with).


    With a c.p.c. present however there would seem to be a risk of a L-c.p.c. fault (especially with T&E where the c.p.c. isn't insulated as if it were a live part), which although wouldn't make any exposed-conductive-parts on that circuit live (as there aren't any) - it would make the c.p.c. itself hazardous live - and so too anything connected to it - e.g. exposed-conductive-parts of other circuits connected to the same DB for instance. Granted the touch voltage on remote parts would likely be much lower than at the fault - but if the disconnection time is really extended that still might not be sufficient to ensure safety.


      - Andy.