Geez:
... but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from ...
This topic came up this afternoon when my self-building chum and I discussed the apparent futility of terminating the CPC in the otherwise empty terminal in a ceiling rose with a standard pendant fitting (2-way, so not looped at the rose). Leaving aside the requirement in Bs 7671 to provide a CPC, there is always the possibility that the fitting may be replaced by a class 1 one.
In answer to the above, if class 2 fitted and CPC terminated correctly => no code; if class 2 fitted and CPC snipped off => C3 (couldn't be worse because no fault to danger); if class 1 fitted and CPC snipped off => C2.
Geez:
... but what would you code a standard class 2 lighting pendent that had no earth connected? there are no exposed conductive parts on the circuit to get a shock from ...
This topic came up this afternoon when my self-building chum and I discussed the apparent futility of terminating the CPC in the otherwise empty terminal in a ceiling rose with a standard pendant fitting (2-way, so not looped at the rose). Leaving aside the requirement in Bs 7671 to provide a CPC, there is always the possibility that the fitting may be replaced by a class 1 one.
In answer to the above, if class 2 fitted and CPC terminated correctly => no code; if class 2 fitted and CPC snipped off => C3 (couldn't be worse because no fault to danger); if class 1 fitted and CPC snipped off => C2.