Bathroom Lights Tripping RCBO

Former Community Member
Former Community Member
Hi all. I have fully rewired my house, completed approx 5/6 weeks ago. Testing passed without fault. Last night the missus pulled the cord for the bathroom lights and apparently they all flashed on for a second and tripped the rcbo. (I have confirmed this) The 4 downlights are Aurora 5W ip65 fittings. Have since turned the fan iso off and remade switch but still tripped. Investigated the cables and their connections, no fault their either. Disconnected all the lights and wago’d off and no trip. At this point I turned the fan back on and whaddyaknow.. it tripped. 


seems as if their is a fault with the fan (opened it up and connection is okay so who knows) as well as the lights? Seems extremely unlikely to have blown together. I can not wrap my head around the issue. Please advise further!!
Parents
  • Not sure if overload or RCD, is there a secret way of checking at the rcbo that I don’t know about?

    Not secret, but some brands helpfully trip to a 'centre' position for the RCD or all the way for an MCB trip.

      - Andy.
Reply
  • Not sure if overload or RCD, is there a secret way of checking at the rcbo that I don’t know about?

    Not secret, but some brands helpfully trip to a 'centre' position for the RCD or all the way for an MCB trip.