Ring Main at Consumer unit

Former Community Member
Former Community Member
My daughter has just had an electrical safety check done and I suspect that the electrician has been over zeleous..

Would anyone care to comment.


There is no grommet where the meter tails enter the consumer unit and the outer insulation stops just short of the knockout.

He has graded this C1.   Now my opinion is that that does not present an  an immediate threat to the safety of personell

It needs fixing but surely only a C2?


More intriguing.  He gives a C3 to the ring circuit because the two legs enter the consumer unit through separate knock outs.  I can't find that in the regs


And finally an old chestnut which has been discussed before.   A C3 because two radial "circuits" are served by a single breaker..  I have always argued that the definition of a circuit is that it is served by a single breaker.  Certainly if both radials were brought to a junction box outside the CU and then connected to the breaker by a single cable it would meet the definition of a radial..


Thanks for your attention

Parents
  • Out of his depth comes to mind… C2 for the tails unless you can stick your finger in and touch something live. We have final ring circuits now because we love a name change but seriously it’s just something he’s made up must be loads of legs passing through different holes just in back boxes. As to two radials on one breaker it’s again perfectly ok.
Reply
  • Out of his depth comes to mind… C2 for the tails unless you can stick your finger in and touch something live. We have final ring circuits now because we love a name change but seriously it’s just something he’s made up must be loads of legs passing through different holes just in back boxes. As to two radials on one breaker it’s again perfectly ok.