Ring Main at Consumer unit

Former Community Member
Former Community Member
My daughter has just had an electrical safety check done and I suspect that the electrician has been over zeleous..

Would anyone care to comment.


There is no grommet where the meter tails enter the consumer unit and the outer insulation stops just short of the knockout.

He has graded this C1.   Now my opinion is that that does not present an  an immediate threat to the safety of personell

It needs fixing but surely only a C2?


More intriguing.  He gives a C3 to the ring circuit because the two legs enter the consumer unit through separate knock outs.  I can't find that in the regs


And finally an old chestnut which has been discussed before.   A C3 because two radial "circuits" are served by a single breaker..  I have always argued that the definition of a circuit is that it is served by a single breaker.  Certainly if both radials were brought to a junction box outside the CU and then connected to the breaker by a single cable it would meet the definition of a radial..


Thanks for your attention

Parents
  • Former Community Member
    0 Former Community Member
    You are welcome to a copy.  How do I get it to you?

    My daughter has already paid for the report and she is of a character that abhors fuss.

    I will  try to persuade to use another electrician to any remedial work.   I am competent to do most of it myself but am unhappy to deal with live meter tails


    I think that a  new CU with RCBOs  would be a worthwhile upgrade even if what you say is tru
Reply
  • Former Community Member
    0 Former Community Member
    You are welcome to a copy.  How do I get it to you?

    My daughter has already paid for the report and she is of a character that abhors fuss.

    I will  try to persuade to use another electrician to any remedial work.   I am competent to do most of it myself but am unhappy to deal with live meter tails


    I think that a  new CU with RCBOs  would be a worthwhile upgrade even if what you say is tru