dcbwhaley:
My daughter has just had an electrical safety check done and I suspect that the electrician has been over zeleous..
Would anyone care to comment.
There is no grommet where the meter tails enter the consumer unit and the outer insu
And finally an old chestnut which has been discussed before. A C3 because two radial "circuits" are served by a single breaker.. I have always argued that the definition of a circuit is that it is served by a single breaker. Certainly if both radials were brought to a junction box outside the CU and then connected to the breaker by a single cable it would meet the definition of a radial..
What are the two circuits? Are they two lighting circuits which have been put onto one M.C.B. for some reason or another, where initially they were two separate circuits on two separate breakers.
314.1
Z.
dcbwhaley:
My daughter has just had an electrical safety check done and I suspect that the electrician has been over zeleous..
Would anyone care to comment.
There is no grommet where the meter tails enter the consumer unit and the outer insu
And finally an old chestnut which has been discussed before. A C3 because two radial "circuits" are served by a single breaker.. I have always argued that the definition of a circuit is that it is served by a single breaker. Certainly if both radials were brought to a junction box outside the CU and then connected to the breaker by a single cable it would meet the definition of a radial..
What are the two circuits? Are they two lighting circuits which have been put onto one M.C.B. for some reason or another, where initially they were two separate circuits on two separate breakers.
314.1
Z.