dcbwhaley:
No. I am merely asking for a second opinion on his conclusions. If he is confident of therm that should cause him no pain.
I have spoken to him and he is adamant that the missing grommet where the tails enter the CU is a C1 and that we should have the DNO disconnect the the power to the house until this can be sorted. His reasoning is if the my daughter was standing on a ladder with his hand on the consumer unit when the insulation finally gave way there was both a risk of electrocution and of falling
My advice to herr is not to touch the CU until the problem is resolved.. And there is a bed for her at dcb-towers if she wishes to follow the EICR advice
This is not an immediate danger - it may be not how he would do it, nor indeed many on here, and should be tidied up in due course, but is a long way from being as serious as suggested.
C1 would be reserved for bare live copper within reach, or an equivalent. Given we are talking about primary insulation intact, metal boxes earthed, what you have describe could be C3 or perhaps C2 depending quite what else is wrong there. Not exactly a matter of life and death.
Perhaps he should take a few foreign holidays once it is permitted again, to re-calibrate his sense of electrical danger. I can recommend Eastern bloc, or south American, installations as being very educational examples of things that are actually quite safe by demonstration, but it does not look like it to our standards.
Mike.
dcbwhaley:
No. I am merely asking for a second opinion on his conclusions. If he is confident of therm that should cause him no pain.
I have spoken to him and he is adamant that the missing grommet where the tails enter the CU is a C1 and that we should have the DNO disconnect the the power to the house until this can be sorted. His reasoning is if the my daughter was standing on a ladder with his hand on the consumer unit when the insulation finally gave way there was both a risk of electrocution and of falling
My advice to herr is not to touch the CU until the problem is resolved.. And there is a bed for her at dcb-towers if she wishes to follow the EICR advice
This is not an immediate danger - it may be not how he would do it, nor indeed many on here, and should be tidied up in due course, but is a long way from being as serious as suggested.
C1 would be reserved for bare live copper within reach, or an equivalent. Given we are talking about primary insulation intact, metal boxes earthed, what you have describe could be C3 or perhaps C2 depending quite what else is wrong there. Not exactly a matter of life and death.
Perhaps he should take a few foreign holidays once it is permitted again, to re-calibrate his sense of electrical danger. I can recommend Eastern bloc, or south American, installations as being very educational examples of things that are actually quite safe by demonstration, but it does not look like it to our standards.
Mike.