Sparkingchip:
I now have a mental picture of these consumer unit tails, I suspect that originally they were pushed right into the consumer unit with the inner single insulation completely concealed and the grommet in place.
A some time the tails have been yanked or dropped due to lack of support dislodging the grommet, exposing the inner single insulation and possibly stressing the terminations.
Quibbling about if they warrant a C1 or several C2s is being pedantic, maybe it’s not a C1, but the outcome is the same, the report is stating it’s a mess that needs tidying up.
Your analysis is almost certainly correct. I suspect that the tails were disturbed during the installation of the smart meter.. And it certainly needs attention.
But it is not a quibble, he outcome is not the same if the fault is a C1 as it would be if it were a C2
If the fault is a C1 the family is advised, by the inspector, to immediately move out of the house to a hotel, put their animals in kennels, and not return until the faults has been rectified which could be several weeks. If a C2 then they can remain in the house, taking care to avoid touching the CU until it is fixed. Given the difficulty of finding an electrician to do the job that represents a considerable sum of money
Sparkingchip:
I now have a mental picture of these consumer unit tails, I suspect that originally they were pushed right into the consumer unit with the inner single insulation completely concealed and the grommet in place.
A some time the tails have been yanked or dropped due to lack of support dislodging the grommet, exposing the inner single insulation and possibly stressing the terminations.
Quibbling about if they warrant a C1 or several C2s is being pedantic, maybe it’s not a C1, but the outcome is the same, the report is stating it’s a mess that needs tidying up.
Your analysis is almost certainly correct. I suspect that the tails were disturbed during the installation of the smart meter.. And it certainly needs attention.
But it is not a quibble, he outcome is not the same if the fault is a C1 as it would be if it were a C2
If the fault is a C1 the family is advised, by the inspector, to immediately move out of the house to a hotel, put their animals in kennels, and not return until the faults has been rectified which could be several weeks. If a C2 then they can remain in the house, taking care to avoid touching the CU until it is fixed. Given the difficulty of finding an electrician to do the job that represents a considerable sum of money