davezawadi (David Stone):
The primary insulation of the tails can be seen or touched, that is your observation. The sheath IS NOT INSULATION, it is mechanical protection. There is no reason to suspect the primary insulation allows contact with live parts, the correct code is C3, requires improvement. This idea of moving out is complete nonsense, as is C1 or C2. The installation does not meet the requirements of the regulations but is not DANGEROUS. If you think this is dangerous, you and I have wildly different visions of reality. I assume you spend all day hiding in bed, unless damaged you cannot get a shock from LV insulation! It is untidy, and needs some work.
Just for information, if these were HV cables at say 33kV you could get a tingle if the shielding were not connected due to capacitive coupling of a small current through the small capacitance to your hand, but you need a very high voltage to make this large enough to feel. Because you might jump back and fall this should probably be a C2, but not with 230V.
I do not know who the "you" refers to in this post, but if itis me you are are misrepresenting me. I am completly in agreement with you. In my opinion the lack of sheath is a C3. There are two other places in the installation where,, at socket entries, where primary insulation is visible and these have been graded C3
The fact that there is no grommet and the primary insulation is in contact with the edge of the knock-out is a seperate and more contentious issue. I have done an experiment with a piece of tail cable and an old back box and found it almost impossible to damage the cable on the edge of a bare knock-out
davezawadi (David Stone):
The primary insulation of the tails can be seen or touched, that is your observation. The sheath IS NOT INSULATION, it is mechanical protection. There is no reason to suspect the primary insulation allows contact with live parts, the correct code is C3, requires improvement. This idea of moving out is complete nonsense, as is C1 or C2. The installation does not meet the requirements of the regulations but is not DANGEROUS. If you think this is dangerous, you and I have wildly different visions of reality. I assume you spend all day hiding in bed, unless damaged you cannot get a shock from LV insulation! It is untidy, and needs some work.
Just for information, if these were HV cables at say 33kV you could get a tingle if the shielding were not connected due to capacitive coupling of a small current through the small capacitance to your hand, but you need a very high voltage to make this large enough to feel. Because you might jump back and fall this should probably be a C2, but not with 230V.
I do not know who the "you" refers to in this post, but if itis me you are are misrepresenting me. I am completly in agreement with you. In my opinion the lack of sheath is a C3. There are two other places in the installation where,, at socket entries, where primary insulation is visible and these have been graded C3
The fact that there is no grommet and the primary insulation is in contact with the edge of the knock-out is a seperate and more contentious issue. I have done an experiment with a piece of tail cable and an old back box and found it almost impossible to damage the cable on the edge of a bare knock-out