if I am designing a circuit where, due to installation conditions, I was required to use SWA 90C XLPE thermosetting cable. The cable is de rated to 70C as it will be bunched with other circuits on a cable tray and then buried in duct in another part of the run. My question is, if I am derating the XLPE to 70C, do I use the data given for 70C PVC thermoplastic cables in the absence of manufacturers data? like treating the XLPE as same as the PVC cable ??
here is the design question
" You are required to calculate the supply circuit for a 41 kW 400 V three-phase injection-moulding
machine with a power factor of 0.87. The 36 m circuit will be run from a distribution board at the
origin of the installation using three-core 600/1000 V 90 ˚C thermosetting steel-wire armoured
cable with circular conductors. Due to the logistics of the installation, the circuit will be run on
existing cable tray. The circuit will run next to seven other loaded circuits, some of which have a
maximum operating temperature of 70 ˚C. All the cables will be run in one flat layer, but without
gaps between.
"