AJJewsbury:Of course, if that's the case, 5 s (2 s TT) disconnection time
Graham - you've mentioned 2s for TT a few times now - yet my copy (411.3.2.4) says 1s - is there a change in the pipeline?
- Andy.
No ... it's me being silly .. an unconscious blunder. I've edited previous post.
For clarity, with TT the default case with U0of 230 V is definitely 0.2 s (Table 41.1/Regulation 411.3.2) and 1 s (Where Regulation 411.3.2.4 applies).
AJJewsbury:Of course, if that's the case, 5 s (2 s TT) disconnection time
Graham - you've mentioned 2s for TT a few times now - yet my copy (411.3.2.4) says 1s - is there a change in the pipeline?
- Andy.
No ... it's me being silly .. an unconscious blunder. I've edited previous post.
For clarity, with TT the default case with U0of 230 V is definitely 0.2 s (Table 41.1/Regulation 411.3.2) and 1 s (Where Regulation 411.3.2.4 applies).