Coming back to this wretched EICR at my daughter's house
An outbuilding used as an office is supplied by a 6mm^2 T&E carried from the house on a catenary wire.and fused at the house at 32A (RCD protected)
In the garage the the 6mm^2 is split into a 2.5mm^2 for sockets and a 1mm^2 for the lighting
This is coded C2 for the inadequate protection and C3 for using T&E outdoors. Both of which seem reasonable
Q1 Can I put a two unit CU in the outbuilding with just a 6amp and 16amp MCB or do | need also to provide a two pole switch?
Q2 What do the great and the good think of using T&E outdoors? Should I replace it with hi-tuf?