This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Outbuilding consumer unit

Former Community Member
Former Community Member
Coming back to this wretched EICR at my daughter's house


An outbuilding used as an office is supplied by a 6mm^2 T&E carried from the house on a catenary wire.and fused at the house at 32A (RCD protected)

In the garage the the 6mm^2 is split into a 2.5mm^2 for sockets and a 1mm^2 for the lighting

This is coded C2 for the inadequate protection and C3 for using T&E outdoors.  Both of which seem reasonable


Q1  Can I put a two unit CU in the outbuilding with just a 6amp and 16amp MCB or do | need also to provide a two pole switch?

Q2  What do the great and the good think of using T&E outdoors?  Should I replace it with hi-tuf?
Parents
  • dcbwhaley:

    It is difficult to find small Cus without RCDs these days and I dislike having RCDs in series


    You could always take the somewhat retrograde step of replacing the CU's RCD main switch with an ordinary one. (I like the BG one - built like a brick dunny.)


Reply
  • dcbwhaley:

    It is difficult to find small Cus without RCDs these days and I dislike having RCDs in series


    You could always take the somewhat retrograde step of replacing the CU's RCD main switch with an ordinary one. (I like the BG one - built like a brick dunny.)


Children
No Data