Coming back to this wretched EICR at my daughter's house


An outbuilding used as an office is supplied by a 6mm^2 T&E carried from the house on a catenary wire.and fused at the house at 32A (RCD protected)

In the garage the the 6mm^2 is split into a 2.5mm^2 for sockets and a 1mm^2 for the lighting

This is coded C2 for the inadequate protection and C3 for using T&E outdoors.  Both of which seem reasonable


Q1  Can I put a two unit CU in the outbuilding with just a 6amp and 16amp MCB or do | need also to provide a two pole switch?

Q2  What do the great and the good think of using T&E outdoors?  Should I replace it with hi-tuf?
Parents
  • Former Community Member
    0 Former Community Member
    dcbwhaley:

    No.  THe C3 is because it has no mechanic protection and is low enough for a six footer to touch

    I suppose protection from UV could be provided by simply wrapping Gaffer tape around it :-)

     


    Strange, its perfectly acceptable to clip a length of T&E down a wall to a light switch that's low enough for a three footer to touch. Is the cable likely to sustain any damage the way it is installed?  Hituf is also not mechanically protected, just a bit tougher than T&E. Cables that are both insulated and sheathed like T&E and Hituf are suitable for touching as far as I'm aware.


Reply
  • Former Community Member
    0 Former Community Member
    dcbwhaley:

    No.  THe C3 is because it has no mechanic protection and is low enough for a six footer to touch

    I suppose protection from UV could be provided by simply wrapping Gaffer tape around it :-)

     


    Strange, its perfectly acceptable to clip a length of T&E down a wall to a light switch that's low enough for a three footer to touch. Is the cable likely to sustain any damage the way it is installed?  Hituf is also not mechanically protected, just a bit tougher than T&E. Cables that are both insulated and sheathed like T&E and Hituf are suitable for touching as far as I'm aware.