fill factor for ducts/trenches

Former Community Member
Former Community Member
hi


what is the fill factor for an underground duct, trench for SWA 400v cables ?
  • I don't think UK regulations stipulate a particular fill factor.


    Good practice, the ability to draw in with relative ease and perhaps leaving room for later additions, would suggest leaving a reaonable amount of space, but the exact figure will depend on the circumstances (e.g. duct length between acess points and number/angle of bends etc.)


    Someone here might have some rules of thunb....


       - Andy.
  • Former Community Member
    0 Former Community Member
    Tables 4C3 and 4C6 will give a general idea of rating factor that is more likely to be the determining criteria rather than how many you can stuff into the duct/trench.


    Regards


    BOD

    stuff into non technical term!
  • Former Community Member
    0 Former Community Member
    thanks for replies, I will search BS7671 for 4C3 and 4C6