Sparkingchip:
What is the tripping current of a Voltage Operated Earth Leakage Circuit Breaker?
They work like a Volt meter. If they detect a certain Voltage between earthed metalwork within an installation, and true Earth, they trip off and open their supply contacts to the load.
The applicable B.S. for V.O.E.L.C.B.s at the time was B.S. 842. It required them to operate at 24 Volts to earth with a 200 Ohm earth electrode, and at 40 Volts with a 500 Ohm earth electrode. Crabtree claimed that theirs were instantaneous in operation. I still find perfectly operational ones today, except that the earth rod may have deteriorated or earthing lead has been pruned through, as it may only have been a 2.5mm2 green insulated solid conductor. The great thing about the test button was that it confirmed not only operation of the unit, but also the effectiveness and condition of the earth rod and earthing lead (earthing conductor). They were very well made and were solid and clunky.
https://www.bing.com/videos/search?q=John+Ward+voltage+operated+earth+leakage&docid=608032099226879187&mid=D18E886DA26FA44990EBD18E886DA26FA44990EB&view=detail&FORM=VIRE
Z.
Sparkingchip:
What is the tripping current of a Voltage Operated Earth Leakage Circuit Breaker?
They work like a Volt meter. If they detect a certain Voltage between earthed metalwork within an installation, and true Earth, they trip off and open their supply contacts to the load.
The applicable B.S. for V.O.E.L.C.B.s at the time was B.S. 842. It required them to operate at 24 Volts to earth with a 200 Ohm earth electrode, and at 40 Volts with a 500 Ohm earth electrode. Crabtree claimed that theirs were instantaneous in operation. I still find perfectly operational ones today, except that the earth rod may have deteriorated or earthing lead has been pruned through, as it may only have been a 2.5mm2 green insulated solid conductor. The great thing about the test button was that it confirmed not only operation of the unit, but also the effectiveness and condition of the earth rod and earthing lead (earthing conductor). They were very well made and were solid and clunky.
https://www.bing.com/videos/search?q=John+Ward+voltage+operated+earth+leakage&docid=608032099226879187&mid=D18E886DA26FA44990EBD18E886DA26FA44990EB&view=detail&FORM=VIRE
Z.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site