For an external socket outlet to be used as a dedicated EV charging point, what are the earthing arrangements ? Given it will be RCD protected. I assuming this socket outlet will be considered as an EV Charging point under the regs.


Is mode 1 not allowed in the UK anymore? I read this in an article done by IET Wiring matter "According to a note in IEC 61851 Mode 1 charging is not permitted in the UK". If so why is it still in the regs?


Thanks.


J
Parents
  • johnwicklover:

    For an external socket outlet to be used as a dedicated EV charging point, what are the earthing arrangements ? Given it will be RCD protected. I assuming this socket outlet will be considered as an EV Charging point under the regs.


    Is mode 1 not allowed in the UK anymore? I read this in an article done by IET Wiring matter "According to a note in IEC 61851 Mode 1 charging is not permitted in the UK". If so why is it still in the regs?


    Thanks.


    J


    Mode 2 charging also uses a standard socket-outlet. This is the "granny lead" people talk about that comes with a new EV.

    Mode 2 leads have an in-cable control box which has some safety features built in, whereas Mode 1 does not.


    Even though Mode 1 charging should not be found on a new car, there needs to be provision for existing vehicles also.


Reply
  • johnwicklover:

    For an external socket outlet to be used as a dedicated EV charging point, what are the earthing arrangements ? Given it will be RCD protected. I assuming this socket outlet will be considered as an EV Charging point under the regs.


    Is mode 1 not allowed in the UK anymore? I read this in an article done by IET Wiring matter "According to a note in IEC 61851 Mode 1 charging is not permitted in the UK". If so why is it still in the regs?


    Thanks.


    J


    Mode 2 charging also uses a standard socket-outlet. This is the "granny lead" people talk about that comes with a new EV.

    Mode 2 leads have an in-cable control box which has some safety features built in, whereas Mode 1 does not.


    Even though Mode 1 charging should not be found on a new car, there needs to be provision for existing vehicles also.