Zoomup:gkenyon:David Bridgman:
If I was running a 10A plus load for Hours, a 16A BS4343 (Commando) socket would be my socket of choice.
Noting of course that BS 7671 prohibits those in domestic premises, because they are not shuttered.
553.1.201 Every socket-outlet for household and similar use shall be of the shuttered type and, for an AC installation, shall preferably be of a type complying with BS 1363.
If the 13 Amp plug is likely to overheat could I not apply 553.1.5 (iii) and use a caravan socket and plug?
Z.
How do you work that out? (iii) applies to a plug and socket-outlet "not complying with BS 1363, BS 546 or BS EN 60309-2"
And regardless, 553.1.201 is not a requirement for a BS 1363 socket-outlets to be used exclusively in household and similar use, it's just a preference, but for all socket-outlets for household and similar use to be shuttered.
I have a 16 A BS EN 60309-2 socket-outlet in my detached garage, but I've taken a decision it's not "household and similar use" because it's for my welder which specifically states it can't be used with a BS 1363-1 plug.
However, I'm sure there will be people who disagree with my decision and will say that the garage is part of the household ...
Zoomup:gkenyon:David Bridgman:
If I was running a 10A plus load for Hours, a 16A BS4343 (Commando) socket would be my socket of choice.
Noting of course that BS 7671 prohibits those in domestic premises, because they are not shuttered.
553.1.201 Every socket-outlet for household and similar use shall be of the shuttered type and, for an AC installation, shall preferably be of a type complying with BS 1363.
If the 13 Amp plug is likely to overheat could I not apply 553.1.5 (iii) and use a caravan socket and plug?
Z.
How do you work that out? (iii) applies to a plug and socket-outlet "not complying with BS 1363, BS 546 or BS EN 60309-2"
And regardless, 553.1.201 is not a requirement for a BS 1363 socket-outlets to be used exclusively in household and similar use, it's just a preference, but for all socket-outlets for household and similar use to be shuttered.
I have a 16 A BS EN 60309-2 socket-outlet in my detached garage, but I've taken a decision it's not "household and similar use" because it's for my welder which specifically states it can't be used with a BS 1363-1 plug.
However, I'm sure there will be people who disagree with my decision and will say that the garage is part of the household ...
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.