If I was running a 10A plus load for Hours, a 16A BS4343 (Commando) socket would be my socket of choice.
Noting of course that BS 7671 prohibits those in domestic premises, because they are not shuttered.
553.1.201 Every socket-outlet for household and similar use shall be of the shuttered type and, for an AC installation, shall preferably be of a type complying with BS 1363.
If the 13 Amp plug is likely to overheat could I not apply 553.1.5 (iii) and use a caravan socket and plug?
Z.How do you work that out? (iii) applies to a plug and socket-outlet "not complying with BS 1363, BS 546 or BS EN 60309-2"
And regardless, 553.1.201 is not a requirement for a BS 1363 socket-outlets to be used exclusively in household and similar use, it's just a preference, but for all socket-outlets for household and similar use to be shuttered.
I have a 16 A BS EN 60309-2 socket-outlet in my detached garage, but I've taken a decision it's not "household and similar use" because it's for my welder which specifically states it can't be used with a BS 1363-1 plug.
However, I'm sure there will be people who disagree with my decision and will say that the garage is part of the household ...
Would that rule out the use of a B.S.4343 socket or plug?
Z.
gkenyon:Zoomup:gkenyon:David Bridgman:
If I was running a 10A plus load for Hours, a 16A BS4343 (Commando) socket would be my socket of choice.
Noting of course that BS 7671 prohibits those in domestic premises, because they are not shuttered.
553.1.201 Every socket-outlet for household and similar use shall be of the shuttered type and, for an AC installation, shall preferably be of a type complying with BS 1363.
If the 13 Amp plug is likely to overheat could I not apply 553.1.5 (iii) and use a caravan socket and plug?
Z.How do you work that out? (iii) applies to a plug and socket-outlet "not complying with BS 1363, BS 546 or BS EN 60309-2"
And regardless, 553.1.201 is not a requirement for a BS 1363 socket-outlets to be used exclusively in household and similar use, it's just a preference, but for all socket-outlets for household and similar use to be shuttered.
I have a 16 A BS EN 60309-2 socket-outlet in my detached garage, but I've taken a decision it's not "household and similar use" because it's for my welder which specifically states it can't be used with a BS 1363-1 plug.
However, I'm sure there will be people who disagree with my decision and will say that the garage is part of the household ...
Would that rule out the use of a B.S.4343 socket or plug?
Z.