For an external socket outlet to be used as a dedicated EV charging point, what are the earthing arrangements ? Given it will be RCD protected. I assuming this socket outlet will be considered as an EV Charging point under the regs.


Is mode 1 not allowed in the UK anymore? I read this in an article done by IET Wiring matter "According to a note in IEC 61851 Mode 1 charging is not permitted in the UK". If so why is it still in the regs?


Thanks.


J
Parents
  • Do we see piles of dead bodies on caravan sites by B.S. 4343 unshuttered sockets? They have been successfully used for years.


    I will use 553.1.5 (iii) get out of jail card and use a B.S. 4343 socket for heavy loads to reduce risks. Along with 133.1.3.


    Common sense must be used in such circumstances.


    Z.
Reply
  • Do we see piles of dead bodies on caravan sites by B.S. 4343 unshuttered sockets? They have been successfully used for years.


    I will use 553.1.5 (iii) get out of jail card and use a B.S. 4343 socket for heavy loads to reduce risks. Along with 133.1.3.


    Common sense must be used in such circumstances.


    Z.