Bending a supply cable

This is a question from a plasterer.


A chipboard panel close to the floor with a service cut-out mounted on it needs to be moved away from the wall in order that it can be plastered. There is a reasonable amount of slack in the meter tails but they could be disconnected from the consumer unit by an electrician as there is an isolator switch on the chipboard panel.


If the chipboard panel is moved away from the wall to provide the space to plaster it then it will involve slightly bending the thick supply cable. Is this a safe move or will it break the insulation and short out internally resulting in a huge explosion?


Would it be safer to remove the chipboard panel by unscrewing the service cut-out from it? This does have the problem that a meter seal has to be broken in order to access its mounting screws.
Parents
  • So it's 80+ year old PILC cable of unknown internal condition, which, if a fault develops when disturbed, could either explode, or start to dramatically overheat - with absolutely no means for emergency switching off. Giving you the opportunity to sit and chat to the nice person on the 105 line while watching the house burn down.


    If the home owner is utterly determined to get nice fresh paster behind the cut-out board, then I'd suggest they pay lots of money to the DNO for a couple of visits.
Reply
  • So it's 80+ year old PILC cable of unknown internal condition, which, if a fault develops when disturbed, could either explode, or start to dramatically overheat - with absolutely no means for emergency switching off. Giving you the opportunity to sit and chat to the nice person on the 105 line while watching the house burn down.


    If the home owner is utterly determined to get nice fresh paster behind the cut-out board, then I'd suggest they pay lots of money to the DNO for a couple of visits.