Sub Boards or Incomer??

Hi

We have a large commercial site fed by 2 onsite substations…

The substations feed panel boards in our side of the subs  i.e. Incomer

The panel boards then feed sub boards within the site, some of which will feed other downstream boards

Our questions are (for condition reporting)

  1. section i… Is the supply characteristic always referring to the incoming supply
  2. when testing a board is the supply protective device the supply feeding this particular board i.e. potentially an mcb in another upstream board that supply's this board … or  is the supply protective device the device on the incoming supply to the site  i.e this will then be the device listed on each board (the same throughout the site)
  3. Is the supply characteristic the supply to the whole site or the supply to just this board
  4. the ZE cannot be reasonably ascertained by test,  but, we also cannot get our supplier to give us this reading by inquiry  What should we do?

 

Parents
  • Hi Andy

    Thanks for the reply

    We have 2 x DNO subs each supplying different areas of our large building (not cross bonded)

    The subs feed 2 large switch rooms that the feed all the boards on site (probably about 100)

    I have tried to get the ZE from our supplier (Scottish power) but they seem to go out of their way to make this info unavailable

Reply
  • Hi Andy

    Thanks for the reply

    We have 2 x DNO subs each supplying different areas of our large building (not cross bonded)

    The subs feed 2 large switch rooms that the feed all the boards on site (probably about 100)

    I have tried to get the ZE from our supplier (Scottish power) but they seem to go out of their way to make this info unavailable