This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Anyone know how to get ZE from Scottish Power ???

Anyone know how to get ZE from Scottish Power

I am just getting the run around….

Parents
  • Agree.

    If you want them to come and  measure it for you, and there  is no fault, they will charge, and considerably more than a normal sparks. 

    If you want them to read you the book value over the phone it will be “less than 0.3 ohms ” for PME or “less than 0.8 ohms ” for TNS or ‘" it’s up to you" if you have TT.

    Note that that “less than 0.8 ohms” will probably co-exist with a PSSC of ‘up to 16kA’  as far as the book is concerned, while in reality there will be a lower PSCC where the cable resistances are higher.

    Mike.

Reply
  • Agree.

    If you want them to come and  measure it for you, and there  is no fault, they will charge, and considerably more than a normal sparks. 

    If you want them to read you the book value over the phone it will be “less than 0.3 ohms ” for PME or “less than 0.8 ohms ” for TNS or ‘" it’s up to you" if you have TT.

    Note that that “less than 0.8 ohms” will probably co-exist with a PSSC of ‘up to 16kA’  as far as the book is concerned, while in reality there will be a lower PSCC where the cable resistances are higher.

    Mike.

Children
No Data