Anyone know how to get ZE from Scottish Power ???

Anyone know how to get ZE from Scottish Power

I am just getting the run around….

Parents
  • Chris Pearson: 
     

    Quote ESQCR 2002:

    Information to be provided on request

    28.  A distributor shall provide, in respect of any existing or proposed consumer’s installation which is connected or is to be connected to his network, to any person who can show a reasonable cause for requiring the information, a written statement of—

    (a)the maximum prospective short circuit current at the supply terminals;

    (b)for low voltage connections, the maximum earth loop impedance of the earth fault path outside the installation;

     

    the words I have highlighted in bold, are why Mike was saying “< 16 kA” and “< 0.35 ohms” (if it's normal PME) and “< 0.8 ohms” if TN-S. They only have to tell you the maximum not the actual … In fact, the actual values can change, and that gets more likely with embedded generation!

Reply
  • Chris Pearson: 
     

    Quote ESQCR 2002:

    Information to be provided on request

    28.  A distributor shall provide, in respect of any existing or proposed consumer’s installation which is connected or is to be connected to his network, to any person who can show a reasonable cause for requiring the information, a written statement of—

    (a)the maximum prospective short circuit current at the supply terminals;

    (b)for low voltage connections, the maximum earth loop impedance of the earth fault path outside the installation;

     

    the words I have highlighted in bold, are why Mike was saying “< 16 kA” and “< 0.35 ohms” (if it's normal PME) and “< 0.8 ohms” if TN-S. They only have to tell you the maximum not the actual … In fact, the actual values can change, and that gets more likely with embedded generation!