Anyone know how to get ZE from Scottish Power ???

Anyone know how to get ZE from Scottish Power

I am just getting the run around….

Parents
  • This is where BS 7671 has its limitations!

    I am guessing that a 600 A fuse would blow in under 5 s with a fault current of around 3 - 5 kA, which would be possible if Ze is 0.08 - 0.05 ohms.

    The DNO must know the size of its fuses and their blow times (could be more than 600 A, but unlikely to be less) and therefore the maximum possible Ze. I feel sure that they would not just say 0.35 ohms because that would be impossible.

    As a matter of interest, how precisely can Ze be measured and with what? I am not thinking of my MFT here. ?

Reply
  • This is where BS 7671 has its limitations!

    I am guessing that a 600 A fuse would blow in under 5 s with a fault current of around 3 - 5 kA, which would be possible if Ze is 0.08 - 0.05 ohms.

    The DNO must know the size of its fuses and their blow times (could be more than 600 A, but unlikely to be less) and therefore the maximum possible Ze. I feel sure that they would not just say 0.35 ohms because that would be impossible.

    As a matter of interest, how precisely can Ze be measured and with what? I am not thinking of my MFT here. ?