Remedy for daisy chained sockets off ring finals and comments on report.

On doing a condition report,have found the tennant has looped several sockets off the kitchen

and 1st floor ring finals.Since the house is fully decorated and has laminate floors,Ive changed 

the 2 x32A mcbs for 20A.As well as a comment on the report should this attract  a C3 as it is not an ideal situation.

                             Regards,

                                           Hz

Parents
  • This is non-compliant but is it potentially dangerous? Perhaps one of you may care to say why this is simply not given a C3, particularly in view of Bills comment above this one? You will need some calculation in your reply, which I would expect the inspector to do!

Reply
  • This is non-compliant but is it potentially dangerous? Perhaps one of you may care to say why this is simply not given a C3, particularly in view of Bills comment above this one? You will need some calculation in your reply, which I would expect the inspector to do!