Remedy for daisy chained sockets off ring finals and comments on report.

On doing a condition report,have found the tennant has looped several sockets off the kitchen

and 1st floor ring finals.Since the house is fully decorated and has laminate floors,Ive changed 

the 2 x32A mcbs for 20A.As well as a comment on the report should this attract  a C3 as it is not an ideal situation.

                             Regards,

                                           Hz

Parents
  • Withe the B20 it is perfectly compliant, arguably over-designed . I suspect with a B32 the load is not an issue in many cases - but it rather depends how much load is on one spur,  and the cable routes in terms of thermals and grouping, rather than the no. of sockets. 

    mike.