Remedy for daisy chained sockets off ring finals and comments on report.

On doing a condition report,have found the tennant has looped several sockets off the kitchen

and 1st floor ring finals.Since the house is fully decorated and has laminate floors,Ive changed 

the 2 x32A mcbs for 20A.As well as a comment on the report should this attract  a C3 as it is not an ideal situation.

                             Regards,

                                           Hz

Parents
  • On testing the kitchen ring final,it was found that 4 of the 8 twin sockets were daisy chained off the cct.The tenant said he had done the work himself before the kitchen was tiled and laminate floor laid.It was decided, because of the potential loads to reduce the mcb to protect the cables.

    Regards,hz

Reply
  • On testing the kitchen ring final,it was found that 4 of the 8 twin sockets were daisy chained off the cct.The tenant said he had done the work himself before the kitchen was tiled and laminate floor laid.It was decided, because of the potential loads to reduce the mcb to protect the cables.

    Regards,hz