Hi I am working through equation 6 for an ambient temperature of 50 degrees for 1mm 90degC thermoplastic cable (Table 4E2A)

11d17c7d56aee28e7d23803363b44f10-original-image.png

I get a correction factor of 0.95 for a 2A load. 

Do i divide the mV/A/m by this factor ? 

The text says multiply, but that would mean the resistance decreases with the increase in temperature (or have I got the sum wrong?)

Parents
  • Former Community Member
    0 Former Community Member

    Thanks Mike,  you two approximations there are both around the 11-12% increase for the effect of temperature, however my 0.95 factor is only half that, from the rules of thumb I would have expected a value closer to 0.88 so it looks like the self-heating of the cable is reducing the effect of the correction factor for ambient in my sum. 

    In you first post you say “if we changed  the Cg, Cs Cd etc are in the direction that they are less than one”  - I just took the Ca straight from the table at 0.82 I (assumed this to be a multiplier. Is this actually the % by which the capacity drops?) 

    I.e should I have flipped that value  (1/0.82) to 122% ? If do the sum then works out to 0.89% which is closer to the expected value

    This discussion has been great for me, it not about the numerical accuracy of the answer, but understand the principles it is based upon

Reply
  • Former Community Member
    0 Former Community Member

    Thanks Mike,  you two approximations there are both around the 11-12% increase for the effect of temperature, however my 0.95 factor is only half that, from the rules of thumb I would have expected a value closer to 0.88 so it looks like the self-heating of the cable is reducing the effect of the correction factor for ambient in my sum. 

    In you first post you say “if we changed  the Cg, Cs Cd etc are in the direction that they are less than one”  - I just took the Ca straight from the table at 0.82 I (assumed this to be a multiplier. Is this actually the % by which the capacity drops?) 

    I.e should I have flipped that value  (1/0.82) to 122% ? If do the sum then works out to 0.89% which is closer to the expected value

    This discussion has been great for me, it not about the numerical accuracy of the answer, but understand the principles it is based upon