Appendix 4, section 6.1 equation 6

Former Community Member
Former Community Member

 

85b1fc637cfb5e3825ed2b73d8b54527-original-image.png

Hi I am working through equation 6 for an ambient temperature of 50 degrees for 1mm 90degC thermoplastic cable (Table 4E2A)

11d17c7d56aee28e7d23803363b44f10-original-image.png

I get a correction factor of 0.95 for a 2A load. 

Do i divide the mV/A/m by this factor ? 

The text says multiply, but that would mean the resistance decreases with the increase in temperature (or have I got the sum wrong?)

Parents
  • Former Community Member
    0 Former Community Member

    Thanks David, the cable for the application is actually a EN 50306 cable - 120degC, I just picked a 90c as an equivalent so I could work though the sum using everyday values from the tables for my understanding before adapting it. The load is electronic, pulling about 1.6A 

    I believe mV/A/M can be calculated (for single phase) from 2 x ohms/KM x K, where K for 70 degrees (for example) is (234.5+70)/(234.5+20)=1.197   so would be 46 for my 20 ohm/KM cable.

Reply
  • Former Community Member
    0 Former Community Member

    Thanks David, the cable for the application is actually a EN 50306 cable - 120degC, I just picked a 90c as an equivalent so I could work though the sum using everyday values from the tables for my understanding before adapting it. The load is electronic, pulling about 1.6A 

    I believe mV/A/M can be calculated (for single phase) from 2 x ohms/KM x K, where K for 70 degrees (for example) is (234.5+70)/(234.5+20)=1.197   so would be 46 for my 20 ohm/KM cable.