Appendix 4, section 6.1 equation 6

Former Community Member
Former Community Member

 

85b1fc637cfb5e3825ed2b73d8b54527-original-image.png

Hi I am working through equation 6 for an ambient temperature of 50 degrees for 1mm 90degC thermoplastic cable (Table 4E2A)

11d17c7d56aee28e7d23803363b44f10-original-image.png

I get a correction factor of 0.95 for a 2A load. 

Do i divide the mV/A/m by this factor ? 

The text says multiply, but that would mean the resistance decreases with the increase in temperature (or have I got the sum wrong?)

Parents
  • So is this 300 metres through a railway tunnel or similar that already has cable supports installed?

    In my head I was picturing a couple of guys trying to pull 300 metres of cable in one length through the roof of a commercial or industrial building, if it’s a tunnel then presumably the cable can be installed without stressing during handling, so does not need to be so robust.

Reply
  • So is this 300 metres through a railway tunnel or similar that already has cable supports installed?

    In my head I was picturing a couple of guys trying to pull 300 metres of cable in one length through the roof of a commercial or industrial building, if it’s a tunnel then presumably the cable can be installed without stressing during handling, so does not need to be so robust.