Power factor (again)

Sorry for yet another question on this topic.

 

I have got sub metering installed on all outgoing submains, I also have a meter on the incoming main

 

Between the main meter and sub meters, I have my power factor correction

 

over a week, I'm getting about 1,500kWh of difference, the sub meters total being higher by that amount compared to the incomer meter.

 

I'd like to say that the power factor correction has effectively saved that number of kWh, is that correct?

Parents
  • There may be CT errors too.  I doubt that these will have been tested together or calibrated.  These errors can soon add up and when you are talking about the difference between two large numbers they can appear considerable.

    If you have power factor correction at the incomer it wont affect current and losses down stream of it.  It should reduce losses upstream.

     

    Im sure there are going to be CT errors, none of it is calibrated, just bought as matching kits if you like. 

     

    yep, I get that the PFC being all together isn't the best for that reason but its probably a good compromise in my situation

Reply
  • There may be CT errors too.  I doubt that these will have been tested together or calibrated.  These errors can soon add up and when you are talking about the difference between two large numbers they can appear considerable.

    If you have power factor correction at the incomer it wont affect current and losses down stream of it.  It should reduce losses upstream.

     

    Im sure there are going to be CT errors, none of it is calibrated, just bought as matching kits if you like. 

     

    yep, I get that the PFC being all together isn't the best for that reason but its probably a good compromise in my situation