This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Videos of EICRs on Youtube

I am interested in comments from anyone on the youtube videos, there are several purporting to show EICR procedures. As most know I am currently researching this, and am collecting data.

https://www.youtube.com/watch?v=RzdQ4kH1G6M

https://www.youtube.com/watch?v=wIlwmp7Ks2w

are of particular interest, ignore any comments I may have left, I want your comments.

 

Kind regards

David

Parents
  • Note that the landlord regs require the inspection to be done by an electrically competent person, but places no constraint on how the testing should be done. In particular it doesn't have to be to BS 7671. So you could hire an electrician to write a report stating how closely the electrical installation follows the principles of fung sui and you would have complied with the regs.

    There is a separate requirement that that the rented installation must comply with BS 7671:2018 at all times, with no allowance for older work. So it is illegal to rent out a property with sockets not RCD protected (although the government guidance says otherwise, which a landlord could use as a defence).

Reply
  • Note that the landlord regs require the inspection to be done by an electrically competent person, but places no constraint on how the testing should be done. In particular it doesn't have to be to BS 7671. So you could hire an electrician to write a report stating how closely the electrical installation follows the principles of fung sui and you would have complied with the regs.

    There is a separate requirement that that the rented installation must comply with BS 7671:2018 at all times, with no allowance for older work. So it is illegal to rent out a property with sockets not RCD protected (although the government guidance says otherwise, which a landlord could use as a defence).

Children
No Data