Rather than hijack an existing thread I thought a new thread might better serve.

A few times I have stated my dislike of the way some folk few acceptance of installations undertaken to earlier editions of our "Regs" being compared to installtions being done very recently.

For those of you (if any) who are not aware of my stance I will repeat it (Yes again, sorry folks).

When doing an EICR/PIR a defect is noted and if that defect was compliant at the time of the actual install then some would not code it at all or perhaps code it more leniently.

I say this is very silly.

A defect should be recorded and if you think it sufficiently impacts on "safety"  (relative safety reallY) then should be coded as appropriate.

We I & T to todays standard and compare it to that.

We might reasonably consider how safe/unsafe we perceive it to be if we compare it to things past.

Those of us who are older and remember earlier Editions of Regs might ,admitadley, be less severe with our coding than a more newbie electrician. That should not be the case but in reality it might well be. We often use that as a mental reference to effect our perception of "safety".

However, no relevance in coding different outcomes should ever be based purely upon the install date (therefore Reg Edition in force at that particular time). It must be purely based on how it compares with our standards now.

So quick answers as to what items we would have not felt aprehensive about in days gone but might concern us a bit more nowadays?

I`ll start of with inclusion of RCDs and Bonding presence/sizing.

Any more?

Parents
  • perspicacious: 
     

    We I & T to todays standard and compare it to that.

    Half way down p473 requires you to fill in “in accordance with BS 7671:2018 (IET Wiring Regulations) as amended to…………………………………………………………………………………………”

    No option to enter 1966.

    My reading of that declaration is that the inspection has been carried out in the manner described by BS 7671:2018 chapter 65, not that the installation has been compared against the rules in BS 7671:2018.

    Chapter 65 itself only mentions compliance with BS 7671 in two places: 651.2, where it notes that older installations are not necessarily unsafe; and 653.2, where it says that the report should include “any non-compliance with the requirements of BS 7671 which may give rise to danger”.

Reply
  • perspicacious: 
     

    We I & T to todays standard and compare it to that.

    Half way down p473 requires you to fill in “in accordance with BS 7671:2018 (IET Wiring Regulations) as amended to…………………………………………………………………………………………”

    No option to enter 1966.

    My reading of that declaration is that the inspection has been carried out in the manner described by BS 7671:2018 chapter 65, not that the installation has been compared against the rules in BS 7671:2018.

    Chapter 65 itself only mentions compliance with BS 7671 in two places: 651.2, where it notes that older installations are not necessarily unsafe; and 653.2, where it says that the report should include “any non-compliance with the requirements of BS 7671 which may give rise to danger”.