Range Cooker Connection Refusal.

A lady today asked me to estimate to do some cooker circuit alterations in her house. She has an old electric range cooker in the kitchen which she is to replace with a new one rated at about 11.2kW.

 

A certain national electrical retailer would not connect up her new and paid for range cooker as the cooker supply is run in 10.00mm2 T&E and protected by a B50 M.C.B. plus R.C.D.

 

The reason given was that the supply is too big and will overload the new cooker.

 

The retailer insisted that the  B50 M.C.B. be replaced by a B40 M.C.B. and the final cooker connection from connection unit to cooker, be run in 6.0mm2, the 10.002 final connection being removed.

 

Comments please.

 

Z.

 

 

 

 

Parents
  • It is likely that much has been lost in translation from the company supplying the cooker via the customer. 

    I agree with Andy that it is likely that the manufacturer’s instructions state a smaller mcb, and that the terminal block on the rear of the cooker is designed for 6mm cable, not 10. To get to the rating, most manufacturers just add the values of all the installed elements, regardless of whether it is possible to use them all at the same time. 

    Regards,

    Alan. 

Reply
  • It is likely that much has been lost in translation from the company supplying the cooker via the customer. 

    I agree with Andy that it is likely that the manufacturer’s instructions state a smaller mcb, and that the terminal block on the rear of the cooker is designed for 6mm cable, not 10. To get to the rating, most manufacturers just add the values of all the installed elements, regardless of whether it is possible to use them all at the same time. 

    Regards,

    Alan. 