Range Cooker Connection Refusal.

A lady today asked me to estimate to do some cooker circuit alterations in her house. She has an old electric range cooker in the kitchen which she is to replace with a new one rated at about 11.2kW.

 

A certain national electrical retailer would not connect up her new and paid for range cooker as the cooker supply is run in 10.00mm2 T&E and protected by a B50 M.C.B. plus R.C.D.

 

The reason given was that the supply is too big and will overload the new cooker.

 

The retailer insisted that the  B50 M.C.B. be replaced by a B40 M.C.B. and the final cooker connection from connection unit to cooker, be run in 6.0mm2, the 10.002 final connection being removed.

 

Comments please.

 

Z.

 

 

 

 

Parents
  •  

    I presume the OP just connected it up and it all works.

    Mike.

    The old range cooker was wired from wall to cooker in 10.0mm2 T&E, no problem. I found a nice two screw per terminal cooker connection plate there. (Must find maker).

     

    M.C.B. changed to B40 type.

     

    Old 10.0mm2 T&E cable for final cooker connection renewed to 6.0mm2 T&E. The old cooker was wired back up to cook tea.

     

    The new cooker has yet to be delivered. So many retailers will not leave the new cooker even though it has been paid for by the customer, and there is room to store it. Perhaps the retailer has to take the old cooker away. It may be contractual.

     

    Z.

     

     

     

     

     

Reply
  •  

    I presume the OP just connected it up and it all works.

    Mike.

    The old range cooker was wired from wall to cooker in 10.0mm2 T&E, no problem. I found a nice two screw per terminal cooker connection plate there. (Must find maker).

     

    M.C.B. changed to B40 type.

     

    Old 10.0mm2 T&E cable for final cooker connection renewed to 6.0mm2 T&E. The old cooker was wired back up to cook tea.

     

    The new cooker has yet to be delivered. So many retailers will not leave the new cooker even though it has been paid for by the customer, and there is room to store it. Perhaps the retailer has to take the old cooker away. It may be contractual.

     

    Z.

     

     

     

     

     