This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Range Cooker Connection Refusal.

A lady today asked me to estimate to do some cooker circuit alterations in her house. She has an old electric range cooker in the kitchen which she is to replace with a new one rated at about 11.2kW.

 

A certain national electrical retailer would not connect up her new and paid for range cooker as the cooker supply is run in 10.00mm2 T&E and protected by a B50 M.C.B. plus R.C.D.

 

The reason given was that the supply is too big and will overload the new cooker.

 

The retailer insisted that the  B50 M.C.B. be replaced by a B40 M.C.B. and the final cooker connection from connection unit to cooker, be run in 6.0mm2, the 10.002 final connection being removed.

 

Comments please.

 

Z.

 

 

 

 

Parents
  • I once suggested that fused connection unit should have clear legible indication on the face plate as to the correct size of fuse to fit if the fuse is replaced. Perhaps by colour coding or preferably in plain text.

     

    Z.

Reply
  • I once suggested that fused connection unit should have clear legible indication on the face plate as to the correct size of fuse to fit if the fuse is replaced. Perhaps by colour coding or preferably in plain text.

     

    Z.

Children
No Data