Metal CU, TT earth and wiring for SPD

Former Community Member
Former Community Member

It appears from everything that I have read that for a TT system it's normal to use a metal consumer unit with normal 100A main incoming switch and RCBO's for circuit protection.

This is based on the unprotected live conductors, meter tails and busbar being well protected and supported reducing the risk of fault. Therefore the risk caused by high earth loop impedance and a live conductor contacting the metal consumer unit is very  low.

It also from catalogues etc to be normal practice to introduce SPD's into these CU's along with a circuit breaker to protect them. This means additional wiring which presumably is not double insulated and does not benefit from additional support.

I could avoid the above with an external SPD but that adds cost and just makes the installation more cluttered.

Am I correct that industry believes it's acceptable to use spd's internally on TT protected CU's along with the additional risk the wiring would cause?

Parents
  • Former Community Member
    0 Former Community Member

    Thanks for the replies, certainly some food for thought.

    I had missed 534.4.7 but I think at least some manufacturers don’t recommend SPD’s downstream of a RCD, will need to check again.

    I hadn’t thought about build up of leakage current when there are multiple RCBO’s in a board, I wonder how likely this is to occur in a domestic environment, I could see it as a major concern in a office building full of IT equipment.

    Looking at the Wylex RCD device from TLC that Chris pointed out, its in a polycarbonate, not metallic case. My understanding that under regulation 421.1.201 this device would be considered as a similar device and would need to be non-combustible in domestic environments? 

    Looking at the data it’s not quite clear if the enclosure is wired with the SPD as a stub, if it’s a stub I think I would need an additional 80A fuse to protect it;  this is something I can ask the manufacturer. But it highlights and area I have been struggling with, we are required to make sure that SPD have OCPD following the manufacturers recommendation but it’s far from easy to find this information.

    Regarding the need for an RCD as a main isolator for an all RCBO board the OSG provides an example consumer unit for TT use with this configuration in fig 3.6.3 (i). There is a similar recommendation in NAPIT OSG section 3.5, page 102. Of course there will be different opinions on the suitability of the suggested solutions.

    But given both documents state that with a metal consumer unit on TT it’s not recommended to combine a standard isolator on the input with dual RCD because of the risk of abrasion to the connecting cables I assume the same conclusion has to be drawn about interconnections for SPD’s.

    I am also wondering if I can put third party SDP’s in consumer units, there are certainly SPD’s available from various companies. But if I can’t mix and match standard RCBO’s and CB’s from different manufacturers in a CU why would it be acceptable to introduce a third party SPD? safe option for now is to use items from same manufacturer.

    Overall it looks like my best way forward is a time delayed RCD on the input and then probably a dual RCD arrangement to keep costs down and do more research on what OCPD is required for various SPD’s on the market. Most boards pre populated with a SDD that I have looked at do not include a OCPD to protect the SPD but don't state if anything is required. Hager is an example where so far I have failed to find any data on what if any OCPD is required.

    It would be fantastic if someone with suitable knowledge and authority would do some joined up thinking and create a document on consumer unit configurations with SPD’s, taking a special look at TT applications. In my opinion (as someone very new to the industry) it’s a complex subject that needs clarifying and making the wrong decisions could increase rather than decrease risk.

Reply
  • Former Community Member
    0 Former Community Member

    Thanks for the replies, certainly some food for thought.

    I had missed 534.4.7 but I think at least some manufacturers don’t recommend SPD’s downstream of a RCD, will need to check again.

    I hadn’t thought about build up of leakage current when there are multiple RCBO’s in a board, I wonder how likely this is to occur in a domestic environment, I could see it as a major concern in a office building full of IT equipment.

    Looking at the Wylex RCD device from TLC that Chris pointed out, its in a polycarbonate, not metallic case. My understanding that under regulation 421.1.201 this device would be considered as a similar device and would need to be non-combustible in domestic environments? 

    Looking at the data it’s not quite clear if the enclosure is wired with the SPD as a stub, if it’s a stub I think I would need an additional 80A fuse to protect it;  this is something I can ask the manufacturer. But it highlights and area I have been struggling with, we are required to make sure that SPD have OCPD following the manufacturers recommendation but it’s far from easy to find this information.

    Regarding the need for an RCD as a main isolator for an all RCBO board the OSG provides an example consumer unit for TT use with this configuration in fig 3.6.3 (i). There is a similar recommendation in NAPIT OSG section 3.5, page 102. Of course there will be different opinions on the suitability of the suggested solutions.

    But given both documents state that with a metal consumer unit on TT it’s not recommended to combine a standard isolator on the input with dual RCD because of the risk of abrasion to the connecting cables I assume the same conclusion has to be drawn about interconnections for SPD’s.

    I am also wondering if I can put third party SDP’s in consumer units, there are certainly SPD’s available from various companies. But if I can’t mix and match standard RCBO’s and CB’s from different manufacturers in a CU why would it be acceptable to introduce a third party SPD? safe option for now is to use items from same manufacturer.

    Overall it looks like my best way forward is a time delayed RCD on the input and then probably a dual RCD arrangement to keep costs down and do more research on what OCPD is required for various SPD’s on the market. Most boards pre populated with a SDD that I have looked at do not include a OCPD to protect the SPD but don't state if anything is required. Hager is an example where so far I have failed to find any data on what if any OCPD is required.

    It would be fantastic if someone with suitable knowledge and authority would do some joined up thinking and create a document on consumer unit configurations with SPD’s, taking a special look at TT applications. In my opinion (as someone very new to the industry) it’s a complex subject that needs clarifying and making the wrong decisions could increase rather than decrease risk.