Regarding figure 8.1 in the OSG (page 94), for the ‘zone 2’ row, the ‘current using equipment’ column appears to make no distinction between ELV/SELV and LV, so:

  • should (12v) SELV downlights (in a ceiling) also be minimum IPX4?
  • what do you think about (12v) MR16 lamps and their connectors being in zone 2 and accessible to a person using the bath (albeit if they stood on the bath edge to reach across to touch them)?

F

Parents
  • Not just the OSG, but the wiring regs say the same as well. IP something 4 please-- i.e. protected against splashing, not that unreasonable.

    701 .512.2
    External Influences
    Installed electrical equipment shall have at least the following degrees of protection:
     (i) In zone 0: IPX7
     (ii) In zones I and 2 : IPX4.
    This requirement does not apply to shaver supply units complying with BS EN 61558-2-5 installed in zone 2 and located where direct spray from showers is unlikely.
    Electrical equipment exposed to water jets, e.g. for cleaning purposes, shall have a degree of protection of at least IPX5.

    Mike

Reply
  • Not just the OSG, but the wiring regs say the same as well. IP something 4 please-- i.e. protected against splashing, not that unreasonable.

    701 .512.2
    External Influences
    Installed electrical equipment shall have at least the following degrees of protection:
     (i) In zone 0: IPX7
     (ii) In zones I and 2 : IPX4.
    This requirement does not apply to shaver supply units complying with BS EN 61558-2-5 installed in zone 2 and located where direct spray from showers is unlikely.
    Electrical equipment exposed to water jets, e.g. for cleaning purposes, shall have a degree of protection of at least IPX5.