BS 7671 Section 521.8.3

Former Community Member
Former Community Member

Section 521.8.3 of BS7671 states: Where two or more circuits are terminated in a single junction box this shall comply with BS EN 60670-22. My question is what if several circuits will terminate in a single wiring device back box which are usually  manufactured to comply with   BS EN 60670-1.

Parents
  • I prefer the definition found in the 13th edition:

    Circuit. “An arrangement of conductors for the purpose of carrying current”.

    Starting  a new “circuit” at a protective device makes no sense. 

    The current modern definition should be renamed.

     

    Z.

Reply
  • I prefer the definition found in the 13th edition:

    Circuit. “An arrangement of conductors for the purpose of carrying current”.

    Starting  a new “circuit” at a protective device makes no sense. 

    The current modern definition should be renamed.

     

    Z.